The fire resistance rating of a separation extending 10 ft (3050 mm) from a set of stairs shall not be required to exceed 1 hour where openings have a minimum of what fire protection rating?
Correct Answer: B
Comprehensive and Detailed Step-by-Step Explanation: Fire Resistance and Stair Separation: According to NFPA 101 (Life Safety Code), Section 7.2.2.5, where a fire-rated separation extends 10 feet from a stair enclosure, the separation fire resistance does not need to exceed 1 hour if the openings have a ½-hour fire protection rating. Why ½ Hour is Acceptable: Openings with a ½-hour fire protection rating are sufficient to limit fire spread in lower-risk scenarios. This exception applies to areas where the separation is minimal but still provides adequate protection to occupants using the stairway. Other Options Explained: Option A (2 hour): Not required for this scenario. Option C (1 hour): The wall may be 1 hour, but the openings need only ½ hour. Option D (1 ½ hour): Exceeds the requirements. Summary: Openings must have a minimum ½-hour fire protection rating where the fire resistance-rated separation extends 10 feet from a set of stairs.