In new health care occupancies, unattended soiled linen receptacles that exceed the permitted capacity must be located in which one of the following locations?
Correct Answer: C
In health care occupancies, soiled linen receptacles pose a fire and contamination risk if they exceed allowable capacity. According to NFPA 101, Life Safety Code, Section 18.7.5.7: Soiled linen receptacles exceeding 32 gallons (121 liters) in capacity must be stored in a hazardous area (C). A hazardous area is a space specifically designed with fire-rated enclosures and safety measures to contain risks associated with combustible materials. Corridor (A): Storing large soiled linen containers in corridors is prohibited to ensure clear egress pathways. Nurses station (B) and Patient room (D): These are not designated hazardous areas and are inappropriate for storing excessive amounts of soiled linens. Reference: NFPA 101, Section 18.7.5.7: Storage and location requirements for soiled linen and trash receptacles.