Question 2/25

A PV system installation utilizes micro inverters connected to each module of the array. Each micro inverter has a nominal rated output of 250WV. Single phase. The microinverters are listed so that multiple inverters may be connected in parallel to a single feeder circuit, and each inverter has ancable and connector rated for
30A. What is the MAXIMUM number of inverters that may be wired together on a single 30A feeder circuit?

LEAVE A REPLY

Your email address will not be published. Required fields are marked *

Question List (25q)
Question 1: Most electric service providers require interactive PV equip...
Question 2: A PV system installation utilizes micro inverters connected ...
Question 3: An installer is using 1/2 in lag boits to secure roof-monito...
Question 4: A site has a known magnetic declination of 14 west. What sho...
Question 5: An installer was asked to provide a means to measure the vol...
Question 6: A homeowner is concerned that a 6kWdc PV system might be exp...
Question 7: An 8KWsc roof-mounted array is placed on a school building. ...
Question 8: The NEC requires that PV systems installed on dwellings inco...
Question 9: Which of the following voltages should be included on the dc...
Question 10: Which is a requirement for designated battery rooms?...
Question 11: A bank of batteries with capability of supplying 250A and a ...
Question 12: A PV connection is being made at the center of a 300 ft. lon...
Question 13: Insulation resistance testing is being performed on the cond...
Question 14: A project is using a PV module with a 25-38dc maximum power ...
Question 15: Which circuits are on the utility side of a service point?...
Question 16: A AWG THWN-2 PV output conductors from two PV arrays are run...
Question 17: A residential PV system uses two 120.240Vac utility-interact...
Question 18: An 8 AWG bare copper equipment ground conductor (EGC) is wir...
Question 19: According to the NEC, where on a residential PV system MUST ...
Question 20: The following dc portion of a PV schematic (functionally gro...
Question 21: Which of the following is an NEC-indicate means to identify ...
Question 22: An installer troubleshooting a ground-mounted array finds It...
Question 23: An installer has decided to use 31 in. long. 3.1/2 in diamet...
Question 24: A grid-interactive PV system with battery backup is being in...
Question 25: Which of the following requires a UL listing or its equivale...