Question 24/25

A grid-interactive PV system with battery backup is being installed with a ground-mounted PV array located
200 ft, from the inverter and batteries. The dc PV output circuit has overcuit has overcurrent protection rated from 30A. To reduce voltage drop between the array and batteries, the output circuit wire size was determined to be 6 AWG. The fused dc disconnect between the inverted and batteries is rated for 300A. What is the required size of the equipment grounding conductor between the metal battery case and the inverter?

LEAVE A REPLY

Your email address will not be published. Required fields are marked *

Question List (25q)
Question 1: Most electric service providers require interactive PV equip...
Question 2: A PV system installation utilizes micro inverters connected ...
Question 3: An installer is using 1/2 in lag boits to secure roof-monito...
Question 4: A site has a known magnetic declination of 14 west. What sho...
Question 5: An installer was asked to provide a means to measure the vol...
Question 6: A homeowner is concerned that a 6kWdc PV system might be exp...
Question 7: An 8KWsc roof-mounted array is placed on a school building. ...
Question 8: The NEC requires that PV systems installed on dwellings inco...
Question 9: Which of the following voltages should be included on the dc...
Question 10: Which is a requirement for designated battery rooms?...
Question 11: A bank of batteries with capability of supplying 250A and a ...
Question 12: A PV connection is being made at the center of a 300 ft. lon...
Question 13: Insulation resistance testing is being performed on the cond...
Question 14: A project is using a PV module with a 25-38dc maximum power ...
Question 15: Which circuits are on the utility side of a service point?...
Question 16: A AWG THWN-2 PV output conductors from two PV arrays are run...
Question 17: A residential PV system uses two 120.240Vac utility-interact...
Question 18: An 8 AWG bare copper equipment ground conductor (EGC) is wir...
Question 19: According to the NEC, where on a residential PV system MUST ...
Question 20: The following dc portion of a PV schematic (functionally gro...
Question 21: Which of the following is an NEC-indicate means to identify ...
Question 22: An installer troubleshooting a ground-mounted array finds It...
Question 23: An installer has decided to use 31 in. long. 3.1/2 in diamet...
Question 24: A grid-interactive PV system with battery backup is being in...
Question 25: Which of the following requires a UL listing or its equivale...