Question 14/147

After the PowerEcho is installed, the default user name is admin. After logging in for the first time and changing the password, if you forget the password, you can retrieve and reset the password through project verification.

LEAVE A REPLY

Your email address will not be published. Required fields are marked *

Question List (147q)
Question 1: What is the maximum IT load supported by the FusionModule200...
Question 2: The EPO status interface of UPS5000-E can choose open or nor...
Question 3: If the FusionModule800 adopts the down pipe, what is the min...
Question 4: The NetEco management system supports user decentralization ...
Question 5: Two UPS5000-E (50kVA power modules) 150kVA, rack 1+1 redunda...
Question 6: What are the possible reason of the excessive noise of the N...
Question 7: If the UPS5000-400K cuts the bypass and closes the maintenan...
Question 8: At present, in the design of the data center, the part ( ) t...
Question 9: UPS5000-A supports the adjustable number of battery cells, w...
Question 10: The relevant standards stipulate that the voltage drop of th...
Question 11: The dry contact signal of UPS5000-E does not support the rem...
Question 12: UPS5000-E can accept the input voltage within the range of (...
Question 13: Huawei's main temperature control solution for small and med...
Question 14: After the PowerEcho is installed, the default user name is a...
Question 15: If a project requires the management system to be connected ...
Question 16: The access control management function of NETECO cannot modi...
Question 17: Traditional UPS. The number of battery cells is not adjustab...
Question 18: Which of the following cladding scenarios does FusionMoudle2...
Question 19: What sensor does FusionModule2000 use to detect whether the ...
Question 20: What security mechanisms does NetEco6000 management system u...
Question 21: What of the following statement of FusionModule2000 v3.0 ver...
Question 22: APM, NR and other UPS products need to be derated at 30 degr...
Question 23: The 2.4G antenna on ECC800 should be installed in ()....
Question 24: Access to the ECC800 by wireless networking is not supported...
Question 25: Users can modify the login password in the () menu of the EC...
Question 26: When the device interface uses the MODBUS-RTU protocol, ( ) ...
Question 27: In this agenda, the refrigerant has undergone the change pro...
Question 28: Which of the following features are standard features of NET...
Question 29: Batteries of different capacities, different specifications,...
Question 30: In FusionModule1000B series solutions, when 2N power supply ...
Question 31: The operating temperature range of FusionModule800 is -40-45...
Question 32: The FusionModule800 does not need to be charged with refrige...
Question 33: Which of the following alarm functions does the main circuit...
Question 34: FusionModule2000UPS is listed as an integrated UPS and suppo...
Question 35: When a fire breaks out in the box and the fire extinguishing...
Question 36: The UPS5000-E (25-75kVA) bypass module has a maximum output ...
Question 37: UPS5000-A has built-in SNMP and ModBus card, which reduces t...
Question 38: If the customer's load cannot be powered off, what should be...
Question 39: Which is not part of the routine maintenance item of the ECC...
Question 40: What methods does the FusionModule800 power input support?...
Question 41: Which of the following fan control modes are supported by Ne...
Question 42: NETCOL5000-C needs to manually adjust the water valve to the...
Question 43: UPS5000-E only needs to select ( ) to easily realize the N+X...
Question 44: After installing the top-out fan on the UPS5000, you need to...
Question 45: The ECC800 is the core component of local management of the ...
Question 46: Which of the following is a component of Huawei's indirect e...
Question 47: UPS5000-series modular UPS product features are similar to w...
Question 48: Which type of circuit breaker used in the sub-circuit of the...
Question 49: What is the range of the number of battery cabinets in the F...
Question 50: What core differentiated features of FusionModule800 can shi...
Question 51: What is the lightning protection level of the integrated UPS...
Question 52: Fusionlodule500 uses natural heat dissipation....
Question 53: ( ) indicates the amount of electricity that a fully charged...
Question 54: During the use of the battery pack, the appearance is normal...
Question 55: The form of humidifier adopted by the row-level chilled wate...
Question 56: The smart ETH socket supports up to () cascades....
Question 57: During the use of the battery, in order to reduce the deteri...
Question 58: FusionModule800 version 3.0 supports face recognition functi...
Question 59: PDU8000 precision power distribution cabinet supports the mo...
Question 60: Which of the following voltage systems does the UPS5000-E su...
Question 61: The main unit of UPS5000-(DKVA power module) occupies a smal...
Question 62: Three groups of 9AH battery packs are connected in parallel ...
Question 63: Which of the following components can control the lighting i...
Question 64: The NETCol5000-A36W air conditioner has a light load initial...
Question 65: In the UPS5000 configuration, the power supply reliability l...
Question 66: When the ECC800 detects that the connection signal to the de...
Question 67: Which of the following descriptions for the configuration of...
Question 68: Which of the FusionModule800 needs on-site construction surv...
Question 69: The bypass module of UPS5000-E-200K (50kVW power module) is ...
Question 70: The access control management function of the Netco6000 mana...
Question 71: Common monitoring software structures include B/S and C/S st...
Question 72: Which of the following are indoor products of Huawei data ce...
Question 73: Huawei NECOL5000-A row-level precision air conditioner elimi...
Question 74: Regarding the overload capacity of UPS5000-E, which of the f...
Question 75: What is the size of the screen of the air conditioner of Fus...
Question 76: The location of the data center needs to be evaluated () fac...
Question 77: When the internal short circuit of the battery occurs, the c...
Question 78: To modify the plan view of the ECC800 micro-module, you need...
Question 79: Compared with NXR, which of the following indicators of UPS5...
Question 80: What methods does Fusi onllodul e800 air conditioner configu...
Question 81: When the inspection, maintenance and repair of electrical in...
Question 82: When the Huawei air-cooled air-conditioning compressor is tu...
Question 83: Fusionllodule2000 UPS is listed and configured?...
Question 84: ECC800 does not support historical data export....
Question 85: What is the possible cause of the high discharge temperature...
Question 86: The temperature control laboratory has passed the GMPI certi...
Question 87: The maximum charging capacity of UPS5000-E is ()...
Question 88: UPS5000-E can maintain high efficiency in a wide load range ...
Question 89: Which of the following technology or solution can reduce PUE...
Question 90: The similar models of Eaton and UPS5000-A 30kVA120kVA are ()...
Question 91: Which of the following modules are included in the UPS5000-E...
Question 92: RH2288 server supports () power input....
Question 93: When a user uses the NETECC APP on the PAD to query the PUE ...
Question 94: What components can the NetCol 8000-C room-level chilled wat...
Question 95: Which of the following functions does PDU8000 precision powe...
Question 96: NETECO's report functions are displayed in various forms, wi...
Question 97: All fire-fighting cables running in the FusionModule1000 are...
Question 98: What is the maximum capacity of the power module of the UPS5...
Question 99: One sunroof actuator can drive up to () sunroof solenoid val...
Question 100: Which of the following certifications has the PDU8000 precis...
Question 101: What is the cabinet depth of Huawei Micro Module 2000? (Mult...
Question 102: The optional temperature and humidity sensor of UPS5000 does...
Question 103: UPS5000-E (50kVA power module) single rack can accommodate u...
Question 104: () can convert POE signal into WIFI signal....
Question 105: When the NetCol8000-C room-level chilled water intelligent t...
Question 106: Which type of compressor is used in new room-level air cooli...
Question 107: The function of the check valve in the NetCol5000-A air cond...
Question 108: UPS5000-E 100kVA, the input switch to be selected by the mac...
Question 109: Huawei's main temperature control solution for small and med...
Question 110: When the power density of a single cabinet is greater than 1...
Question 111: Which of the following functions belong to the FusionModule2...
Question 112: The FusionModule2000 battery is listed in the scene, support...
Question 113: ATS (Automatic Transfer Switch) must overflow the manual ope...
Question 114: The technical essential of the vacuum pumping action of the ...
Question 115: When NETCOL5000-C is debugging the drainage equipment, lift ...
Question 116: What are the factors that affect the service life of the bat...
Question 117: The UPS5000-E battery adopts the design of no center line, w...
Question 118: FusionModule2000 IT cabinet seismic rating?...
Question 119: In ECO mode, when the input is stable, the UPS works in () s...
Question 120: In order to realize the remote notification of the alarm tim...
Question 121: Huawei Neteco network management supports mobile APP managem...
Question 122: UPS5000-E (25-125kVA) does not support the Battery function....
Question 123: What is the channel width of Huawei FusionModule2000?...
Question 124: The domestic power supply system is 380v/50Hz....
Question 125: A single row of FusionModule 2000 supports a maximum of 48 c...
Question 126: Huawei air-cooled air conditioners (25kw and 42kw) one indoo...
Question 127: What operations can be performed in the NetEco "Report Task"...
Question 128: What are the i3 features of FusionModule2000 V3.0 include? (...
Question 129: One NetCol520 chilled water distribution units can maximum s...
Question 130: NETECOL can assign operation rights to user groups, or direc...
Question 131: When calculating the battery capacity, the battery discharge...
Question 132: What are the alarm management functions supported by the ECC...
Question 133: BCB-BOX is an optional part of UPS5000-E, used for connectio...
Question 134: A single row of FusionModule2000 supports a maximum of ( ) c...
Question 135: What are the certifications of FusionModule500&amp;FusionMod...
Question 136: The skylight actuator can control the reversing skylight of ...
Question 137: Which of the following are the working modes of the runner n...
Question 138: Regarding the circuit breaker statement, which of the follow...
Question 139: When the distance between the outdoor unit and the sea is 0....
Question 140: In the single cabinet configuration scenario, which of the f...
Question 141: A system is configured with 15min battery backup time, and t...
Question 142: NETCOL5000-A35KW uses an electronic expansion valve....
Question 143: In the parallel steps of the UPS5000-E, the reason for using...
Question 144: When creating a camera in NETECO, in addition to obtaining t...
Question 145: FusionModule800 3.0 closed channel hot and cold channels are...
Question 146: FusionModule500&amp;FusionModule800 remote WEB interface mon...
Question 147: In a project that requires the deployment of three-layer tem...