You are allowed to use a calculator for this question. The total power consumption of the ICT equipment in a rack is 6 kW. The equipment is traditional ICT equipment with a Delta-T of approximately 11 °C / 20 °F. Calculate the approximate CFM required to cool the equipment in the rack.
Correct Answer: B
To calculate the cooling airflow requirement for ICT equipment, you can use the formula: CFM=Power (kW)×3160ΔT(°F)\text{CFM} = \frac{\text{Power (kW)} \times 3160}{\Delta T (\text{°F})}CFM=ΔT(°F)Power (kW)×3160 For equipment consuming 6 kW with a Delta-T of 20°F: CFM=6×316020=948≈1,000 CFM\text{CFM} = \frac{6 \times 3160}{20} = 948 \approx 1,000 \, \text{CFM}CFM=206×3160=948≈1,000CFM Detailed Explanation: This formula provides an estimate of the cubic feet per minute (CFM) of air required to cool the equipment based on its power consumption and the temperature difference (Delta-T) between intake and exhaust. The Delta-T represents the cooling effectiveness of the airflow. EPI Data Center Specialist References: EPI recommends using this calculation for determining airflow requirements in data centers, ensuring that cooling systems are adequately sized to maintain equipment within safe temperature limits.