Correct Answer: A
Minimum prescriptive dimensions are not themselves a component added into a calculated fire-resistance time. Therefore, option A is the exception.
IBC Section 602.4 states that a mass timber element's required fire resistance can be based on the fire- resistance contribution of the mass timber, the noncombustible protection, or a combination of those two components. Options B, C, and D reflect those permitted approaches.
Minimum dimensions under Section 2304.11 serve a different function. They establish the minimum cross- sectional size and construction characteristics required for qualifying heavy timber or mass timber elements.
A member can satisfy the minimum dimensional requirement without automatically achieving every required one-, two-, or three-hour fire-resistance rating. The structural fire calculation must evaluate the remaining effective section after charring, elevated-temperature effects, applied loading, and any credited protective materials.
The inspector must therefore verify both requirements independently: the installed member must meet the minimum code dimensions and must match the approved fire-resistance design. Increasing a member to the minimum prescriptive size does not by itself replace the required calculation, tested assembly, or approved protection system.
References/Topics: 2021 IBC Sections 602.4, 703.2, 722.7 and 2304.11; calculated mass timber fire resistance.