A recent power Outage caused email services to go down. A sever administrator also received alerts from the datacenter's UPS.
After some investigation, the server administrator learned that each POU was rated at a maximum Of 12A.
INSTRUCTIONS
Ensure power redundancy is implemented throughout each rack and UPS alarms are resolved.
Ensure the maximum potential PDU consumption does not exceed 80% or 9.6A).
a). PDU selections must be changed using the pencil icon.
b). VM Hosts 1 and 2 and Mail Relay can be moved between racks.
c). Certain devices contain additional details