The isolation room is supplied with 300 cfm (142 L/s) of HEPA filtered air. The return air grille is located in the ceiling and has been balanced to 150 cfm (71 L/s). The room is monitored with a differential pressure sensor, and the sensor is sending an alarm signal to the nurse's station. Which of the following BEST describes the problem?
Correct Answer: A
Comprehensive and Detailed Explanation: Airflow Analysis: Supply = 300 cfm, Return = 150 cfm, Toilet Exhaust = 25 cfm. Total exhaust = 150 + 25 = 175 cfm. Net airflow = 300 - 175 = +125 cfm (positive pressure). AIIR Requirements: ASHRAE Standard 170, Section 7.2.1, mandates negative pressure for Airborne Infection Isolation Rooms (AIIRs), meaning exhaust must exceed supply. Here, the room is positive (+125 cfm), triggering the pressure sensor alarm. Problem Identification: The toilet exhaust (25 cfm) is insufficient to offset the supply, failing to achieve negative pressure. AIIRs typically require 50-75 cfm exhaust per toilet (Table 7.1), so 25 cfm is inadequate. Option Analysis: A: Correct-insufficient exhaust explains the positive pressure in an AIIR. B: An open door would reduce pressure differential but not explain the airflow imbalance. C/D: Protective Environment (PE) rooms require positive pressure, which aligns with the +125 cfm, but the alarm suggests an AIIR (negative pressure) context.